RowE
Member
- Location
- Dumas Tx. 79029
I have an switch rack on an oil and gas location. The switch rack is made up of 2 pieces of 2" rigid conduit cemented in the ground with several pieces of unistrut clamped between the 2 pieces of rigid to mount the enclosures on the service is appox 1/4 to 1/2 mile away in most applications. urd is ran underground to the switch rack at the production site and stubs into a disconnect on the rack. At this point the grounded conductor is bonded to the enclosuse inside the 30A disconnect and stops there. The production unit has an electric motor on skid. An equipment grounding conductor is bonded to the motor and skid runs along the conduit underground and attaches to a ground rod at the rack and clamped to one of the 2" poles of the switch rack. Each enclosure is bolted to the strut using bolts and spring nuts. I have a problem with the strut clamps and painted enclosures that do not appear to have been strip of paint being my effective ground fault path to the grounded conductor. Is this effectively grounded?