slc410
Electrician
- Location
- Madison wi
- Occupation
- Electrician
I just started working for a company wiring cabinet panels and ran across what I believe is a tap violation. Main power enters the cabinet and terminates on a 150A breaker. The load side of the breaker then runs approximately 5 feet then terminates into a distribution block (tap). Here is where the problem begins, out of the distribution block there are several #14awg wires which then run to various small breakers which are no more than a couple feet away from the block all within the same panel board.
My concern is what is going to keep the #14's from turning into molten magma if there would ever be a ground fault to the backplane of the panel?
Its my understanding that the tap conductors can be no smaller than 10% of the breaker feeding the taps.
My concern is what is going to keep the #14's from turning into molten magma if there would ever be a ground fault to the backplane of the panel?
Its my understanding that the tap conductors can be no smaller than 10% of the breaker feeding the taps.