Quick question fella's: We have a 120/208V lighting panel being fed directly from a breaker in our substation. A question has come up regarding where this system should be bonded. In my opinion the 120/208 panel is considered a sub panel and the little green screw should not be installed. Your thoughts please!
 
Quick question fella's: We have a 120/208V lighting panel being fed directly from a breaker in our substation. A question has come up regarding where this system should be bonded. In my opinion the 120/208 panel is considered a sub panel and the little green screw should not be installed. Your thoughts please!

It appears I put this in the wrong place. I'm sure a Mod can help.
 
Quick question fella's: We have a 120/208V lighting panel being fed directly from a breaker in our substation. A question has come up regarding where this system should be bonded. In my opinion the 120/208 panel is considered a sub panel and the little green screw should not be installed. Your thoughts please!
Assuming when you say "our" substation it means on the consumer side of the service point, then you are correct.
 