Hi guys, here I have this hypothetical scenario.
We have an effective ground fault current path, an excellent 8 copper EGG, suddenly someone who didn't know much about electricity decided to change the EGC to another type of EGC material with an impedance of 9.5 ohms, but the phase conductor is an excellent 8 AWG wire and has an impedance of 0.05 (9.5 + 0.05 omhs = 10 omhs)
Now there is a ground fault, 120V ÷ 10 = 12A, but the OCPD breaker is rated 30A, therefore it does not trip, now we could say that we no longer have an effective ground fault current path because the installation does not meet the code requirments for the EGFCP definition. However, the question is: Would someone be exposed to receiving a possible electric shock? or Could we assume that the installation continues to be safe since the neutral and the EGC are linked together at one point (MBJ)? What would be the load metal enclouse voltage to earth? 0 V?
We have an effective ground fault current path, an excellent 8 copper EGG, suddenly someone who didn't know much about electricity decided to change the EGC to another type of EGC material with an impedance of 9.5 ohms, but the phase conductor is an excellent 8 AWG wire and has an impedance of 0.05 (9.5 + 0.05 omhs = 10 omhs)
Now there is a ground fault, 120V ÷ 10 = 12A, but the OCPD breaker is rated 30A, therefore it does not trip, now we could say that we no longer have an effective ground fault current path because the installation does not meet the code requirments for the EGFCP definition. However, the question is: Would someone be exposed to receiving a possible electric shock? or Could we assume that the installation continues to be safe since the neutral and the EGC are linked together at one point (MBJ)? What would be the load metal enclouse voltage to earth? 0 V?
Last edited: