In your case would the heaters be a continuous load? If so 13.3x2=26.6amps than if it’s continuous 26.6x125%=33.25ampsHaving a brain fart I have heaters 2pole 208 draw 13.3 amps why can't I run number 10s with a 30a breaker to feed two instead of running dedicated ckts for each thus needing less spaces in a panel that's almost full ready?
Sent from my SM-G986U using Tapatalk
Oh was 13.3 the rating of two heaters combined? I thought you meant each one was 13.3.424.3 says fixed infared heater's shall be permitted to be supplied from branch circuits not rated more then 50 amps
13.3x1.25=16.25
16.25x3=48.75
To me I can put three on one circuits and be good
Sent from my SM-G986U using Tapatalk
No there is notIs there anything from the Mfgr that states a maximum OCPD size for the heater?