I'm planning on a couple of 40 amp(480 3 phase) branch circuits for six (480 1 phase) heaters, the heaters themselves only draw about 15 amps. Is there anything that allows you to downsize the whip to the heater? Or do I need to run #8's all the way?

I've been through Art. 424 and haven't seen anything allowing it. I wasn't planning on using any supplemental OCP at the heaters themselves.

Thanks.
 
I'm planning on a couple of 40 amp(480 3 phase) branch circuits for six (480 1 phase) heaters, the heaters themselves only draw about 15 amps. Is there anything that allows you to downsize the whip to the heater? Or do I need to run #8's all the way?

I've been through Art. 424 and haven't seen anything allowing it. I wasn't planning on using any supplemental OCP at the heaters themselves.

Thanks.

If your OCPD is rated for 40A protection, then your wire needs to carry that. But you know that. No I know of nothing that allows you to downsize the whips. As a thought, why are you running 40amps and, therefore, using eights? With Dennis, I'm wondering why you don't just run a 20A circuit to each. But maybe it has to do with design or distance, or whatever....
 
Sorry guys, didn't mean to confuse you.

I'm using a Fostoria factory made contactor panel capable of two 50 amp 3 phase circuits. I have six single phase heaters to wire into these two 3 phase circuits. So, 3 heaters per circuit at 15 amps(single phase) apiece.

I wasn't sure if you could downsize whips since it's allowed for light fixtures and this wasn't feeding a receptacle, but a known load.

http://www.google.com/products/cata...a=X&ei=FADoTuzfN8OyiQKVrIWjBw&ved=0CE8Q8gIwAA

The customer purchased all of this, I just have to install it.
 
Does the heaters draw 15 amps or is that what size circuit needed for individual install.

If actual rating were just a little lower only a 30 amp circuit would be required to run 3 balanced across phases.

I have done exactly what you are describing less the fostoria controller before, but heaters were only like 1500 or 2000 watts and it worked with a 20 amp circuit.

Next question for your installation is whether or not heaters can be on a 35 or 40 amp circuit, you may need overcurrent protection at each heater either way.
 
Let me know how those IR heaters work, I have been considering buying a bunch of those.

Sure.

Does the heaters draw 15 amps or is that what size circuit needed for individual install.

If actual rating were just a little lower only a 30 amp circuit would be required to run 3 balanced across phases.

I have done exactly what you are describing less the fostoria controller before, but heaters were only like 1500 or 2000 watts and it worked with a 20 amp circuit.

Next question for your installation is whether or not heaters can be on a 35 or 40 amp circuit, you may need overcurrent protection at each heater either way.

They are a 2 lamp 480V 7.3kW heater. About 15.2 amps apiece. I figured 15.2 amps x 2 heaters/phase x 125%=38 amps=40 amp fuses.
 
Sure.



They are a 2 lamp 480V 7.3kW heater. About 15.2 amps apiece. I figured 15.2 amps x 2 heaters/phase x 125%=38 amps=40 amp fuses.

If you balance them across phases and have 3 units you have 1.73 heaters per phase. 15.2 x 1.73 x 125% = just shy of 33 amps.
 