This one makes me scratch my head and makes me nervous a little bit. This solution is very common. 3-pole CB transfers power between two sources without switching the neural. In 3-phase, 4-wire distribution, if the transformers (SDS, not services) are located outside, you have two bonding points at each transformer. This creates an issue for the ground fault coordination before, but the solution was the modified differential ground fault protection scheme.
However, another issue is that will create unwanted circulating current between two sources during normal operation because there are two bonding connections between two SDSs. You can draw a simple diagram to see this. This is big no-no from the safety standpoint. When we use the ATSs for the source transfer, we can always use the 4-pole ATSs and switch the neutral so we don't have this issue. But with 3-pole CB, you can't switch the neutral. Am I missing something here?
However, another issue is that will create unwanted circulating current between two sources during normal operation because there are two bonding connections between two SDSs. You can draw a simple diagram to see this. This is big no-no from the safety standpoint. When we use the ATSs for the source transfer, we can always use the 4-pole ATSs and switch the neutral so we don't have this issue. But with 3-pole CB, you can't switch the neutral. Am I missing something here?