iwire said:Bill I am lost, I have never heard of power wiring being run inside 'innerduct'.
That?s debatable, Don. The rule says to maintain spacing, but does not say how much spacing to maintain. If two sets of conductors are only a half inch apart from each other, but are kept at that same half inch distance for the duration of a 100 foot run, I would say that spacing was maintained. If you have a raceway within a raceway, then the inside raceways will maintain the spacing of the conductors they surround.don_resqcapt19 said:. . . I think you need to derate based on the total number of conductors in all of the innerducts because you will not be maintaining spacing between them as required by 310.15(B)(2)(b).
If anything, I should think it would be worse than having all conductors in a single raceway. The idea of derating for multiple conductors in a raceway has to do with the ability of any given donductor to reject its heat to the surrounding environment. With a large number of conductors in the same area, two things happen. The first is that there is a large number of heat sources. The other is that with the area surrounding any given conductor now being at a higher temperature (due to heat from other conductors), it becomes harder for that one conductor to reject its heat. If you are trying to get rid of heat, it is easier if you are surrounded by cold.mistermudd said:Would a raceway in raceway be any different???
Yes it is very debatable as that is all the subsection says and it only implies that derating would be required if spacing is not maintained and it only does this by its location in the code.(b) More Than One Conduit, Tube, or Raceway. Spacing between conduits, tubing, or raceways shall be maintained.