NEC User

Senior Member
NEC requires limititing conduit fill of multiple wires to 40% maximum within a conduit. My understanding is this is required so insulation doesn't get damaged and cause a fire. Is there a similar fill restriction for innerduct installed within a conduit (a smaller conduit installed within a larger conduit)? I haven't been able to find this restriction in NEC. I think the NEC doesn't specify a restriction because if the conduit gets damaged it won't cause an electrical fire. In this case, whatever the Contractor can fit is suitable.

Please confirm.
 
Thank you for the welcome! This site is great.
I agree the Innderduct can only be filled with wires up to 40% maximum. But is the innerduct limited to only able to fill the conduit up to 40%?
 
NEC requires limititing conduit fill of multiple wires to 40% maximum within a conduit. My understanding is this is required so insulation doesn't get damaged and cause a fire. Is there a similar fill restriction for innerduct installed within a conduit (a smaller conduit installed within a larger conduit)? I haven't been able to find this restriction in NEC. I think the NEC doesn't specify a restriction because if the conduit gets damaged it won't cause an electrical fire. In this case, whatever the Contractor can fit is suitable.

Please confirm.

There are no NEC fill limits if you are talking about data lines.
 