it depends on the motor construction, not power output per se
the NEC gives a table for various types that give starting kva/HP values
from this a the starting current can be determined
eg
50 HP, 460/3 vac, FLA 65 A and assume Code H 7.07 kva/HP (worse case)
starting current = 50 x 7070 / (1.732 x 460) = 445 A or 680%
this assumes no line impedance
motor starting Z = 460/445 = 1.03 Ohm, basically winding Z
determine line Z
assume a 20 v drop (480-460), or you can use actual wire size/length
Vdrop = 20 = 65 Z or Z = 0.31 Ohm
total starting Z = 1.03 + 0.31 = 1.34 Ohm
new inrush = 460/1.34 = 343 or 530%
you also have a voltage drop increase
Vdrop = inrush x line Z = 445 x 0.31 = 138 v or 343 x 0.31 = 106, it will be between the two so use the worse case (which results in the highest inrush) 480 - 106 = 374 vac
new inrush = 374/1.34 = 280 or 430%
make sure you have an issue first
is the V drop an issue? motors a small or large percentage of load, what is main bus drop
nuisance tripping during starting?
is the load type a factor? starting no load or full load, time to ramp up, etc.
etc
if you determine you do, as others have said you can't do much about the motor (other than a different code) you need either a solid state or reduced voltage starter