3 motors, single phase, 1 HP.
Im sizing a battery backup for them.
Unlikely they will all start at the exact moment, but, if I size the system for that, I have LRA of roughly 48A per motor, 144A total, at 240V we have nearly 35K VA.
That seems excessively high for a relatively simple setup. I would never spec a 38kW genset for this installation, but the UPS manufacturers recommend 200% of inrush for all motors.
I haven’t done a ton of these, but I’m getting calls for them, so I guess I should learn.