No.
If your question were transformers in parallel I would be closer to saying yes, but not a definite yes..
Typical inrush currents may be 10X rated current. Saying 10X + 10X isn’t going to be the answer.
There are studies that show inrush from energizing one transformer is about 25% less than energizing 10-15 series transformers.
A few variables..
Magnetizing currents in a transformer are nonlinear.
You have to take into account things like the residual flux in the transformer core, what is the variable there?
The characteristics of the transformer core have to be accounted for. This is almost impossible to model..
The phase of the source when energizing the transformer, or point on wave. Inrush mitigation is the reason for point on wave switching, Also used is second harmonic blocking on relays to stop the nuisance tripping on 87 protection.
Another consideration is the impedance and short circuit power of the supplying source. This may be the most difficult to model.
So it comes down to what cable is feeding the first transformer? (Z)
Short circuit of the circuit
core characteristics of the first transformer, with what value of residual flux
Z of the second cable, with the next transformer and those variables, etc…
ALSO a new dynamic is introduced now with a second (or more) transformers added. This first transformer(X1) inrush helps to lessen the inrush on the second transformer(X2) as X1 now becomes a bottleneck for down line inrush currents.