I'm looking at an application we a cusotmer wants to add a new 480V ATS with generator provision to an existing service. Existing service is a 1200A service with utility padmount feeding 1200A SWBD. Our plan was to intercept the existing underground SE conductors between the transformer and the existing switchboard and insert a SE rated ATS with breakers that we would then re-terminate the existing SE conducotrs to the load side of the ATS.
The issue was broght up that with the existing SE condcutors being 4-wire, when we insert the ATS we will not have an Equipment ground conductor (EGC) between the ATS and the existing switchboard. If there were no requirements for 277 L-N loads off of the existing SWBD then perhaps we could use the existing grounded conductor as an oversized EGC but not sure if there is a need for any L-N loads off of the existing Switchboard (4-Wire SWBD).
Are there any NEC provisions that I may be overlooking here related to the need to add an EGC between the ATS and SWBD for this application?
The issue was broght up that with the existing SE condcutors being 4-wire, when we insert the ATS we will not have an Equipment ground conductor (EGC) between the ATS and the existing switchboard. If there were no requirements for 277 L-N loads off of the existing SWBD then perhaps we could use the existing grounded conductor as an oversized EGC but not sure if there is a need for any L-N loads off of the existing Switchboard (4-Wire SWBD).
Are there any NEC provisions that I may be overlooking here related to the need to add an EGC between the ATS and SWBD for this application?