Is this a correct method of wiring?
View attachment 6953Switch controls light in photo. However, connections are made in the panel. Lampholder neutral connected to the terminal bar. Power (black conductor) from lampholder wire-nut connected (yellow one at the bottom right) to neutral from switch. Black wire from switch is connected to breaker.
Is this a correct method of wiring?
I always heard if using a 2 conductor cable for a switch the white should be the hot one, so when(or is it IF?) is tested it'd show hot all the times. Don't think it's really an NEC thingie. I don't see anything wrong, as far as that is concerned, as long as the white wire is reidentified with a black(or red) tape. Personally I would prefer it that way.
However....
The panel has 8 breakers, no main, and a bunch of grounds connected to the neutral bar. If it's a services panel and the neutral is bonded to the ground, then it's a violation of the 6 main rule. If it's not, than the ground wires can not be terminated on the neutral bar.
The feeder seem to be an SE cable(most likely 2 hots and a neutral) so not sure how getting the ground wires properly connected can be accomplished.
Also, seem the switch box doesn't have a connector(could be wrong)
See section 200.7C 1,2, and 3I always heard if using a 2 conductor cable for a switch the white should be the hot one, so when(or is it IF?) is tested it'd show hot all the times. Don't think it's really an NEC thingie. I don't see anything wrong, as far as that is concerned, as long as the white wire is reidentified with a black(or red) tape. Personally I would prefer it that way.
See section 200.7C 1,2, and 3
Before the days of idiot-proofing the NEC you would use the white as the hot to the switch and the black as the switch leg. Now that the white is required to be re-identified does it really matter?
Before the days of idiot-proofing the NEC you would use the white as the hot to the switch and the black as the switch leg. Now that the white is required to be re-identified does it really matter?
Sounds more like DIYer proofing!!!!Before the days of idiot-proofing the NEC