Inspecting Equipment Prior to Energizing

Status
Not open for further replies.

Gopher

Member
Location
Minnesota
Occupation
Inspector
I am a fairly new inspector and was curious on what your interpretation of inspecting equipment is. A specific example is the electrician is running power for a 30A 208V receptacle for a customer who is purchasing a piece of equipment to plug into this receptacle. Am I correct in saying I cannot complete a final inspection on the installation until the equipment that is being plugged in is on site so I can inspect it for its listing?
 
Generally speaking equipment that is plugged in is not an inspectors concern. It would be the same as holding up a final because the dryer wasn't on site
 
Thanks for the info. I guess I should clarify that I work at a University and a discussion was made that anything that can be plugged into a 120V receptacle is not of our concern, but anything that has "specific" power requirements for an electrician to come install is.
 
Thanks for the info. I guess I should clarify that I work at a University and a discussion was made that anything that can be plugged into a 120V receptacle is not of our concern, but anything that has "specific" power requirements for an electrician to come install is.
Nothing in the NEC about that. You could make it a university policy but it is not a code issue if you're only inspecting the circuit/receptacle installation.
 
Am I correct in saying I cannot complete a final inspection on the installation until the equipment that is being plugged in is on site so I can inspect it for its listing?
I think the key word here is "installation". It's vey hard to install a piece of equipment that's not on site and just as hard to inspect it.

If you are responsible for the correct "installation" of a piece of equipment it would be a good idea to make sure that the listing is correct. Wrong equipment shows up all the time ( at least not exactly what the owner thought they were getting).
 
Each piece of hard wired equipment connected to an electrical source must have a testing laboratory label. (UL or whatever) and it would be within your scope of work to verify the equipment has this label for the installation to be compliant.
A piece of equipment that is connected to the source via a receptacle should not be within your scope of work. Your responsibility stops at the receptacle.
 
I am a fairly new inspector and was curious on what your interpretation of inspecting equipment is. A specific example is the electrician is running power for a 30A 208V receptacle for a customer who is purchasing a piece of equipment to plug into this receptacle. Am I correct in saying I cannot complete a final inspection on the installation until the equipment that is being plugged in is on site so I can inspect it for its listing?
I typically do not plug in anything that I didn't purchase myself.
I don't energize equipment that I didn't purchase myself.
Unless asked to by the owners of the equipment with a warning from me that I am not responsible for that equipment.
 