nizak

Senior Member
Building contractor is asking me to install a residential service on a new construction project.

The panel will be located in the basement.

Conditions are;
- Pea gravel floor with pockets of standing water .
- No permanent or temporary stairs.
- Only access is through outdoor egress with about a 3' step down.

My thoughts are that the inspector will refuse entering because of accessibility.

Thoughts please.
 

eds

Senior Member
If you can access it to build the service, why cant the inspector access it for inspection. I assume it will be built to accommodate the conditions, and be code compliant now and at the finish of the project.
 

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
I looked for an applicable code section and this was the closest I could find:

110.26 Spaces About Electrical Equipment. Access and
working space shall be provided and maintained about all
electrical equipment to permit ready and safe operation and
maintenance of such equipment.

(C) Entrance to and Egress from Working Space.
(1) Minimum Required. At least one entrance of sufficient
area shall be provided to give access to and egress
from working space about electrical equipment.

If you bring you own ladder the space is accessible. Not easily or readily accessible, but that is not the requirement.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I looked for an applicable code section and this was the closest I could find:

110.26 Spaces About Electrical Equipment. Access and
working space shall be provided and maintained about all
electrical equipment to permit ready and safe operation and
maintenance of such equipment.

(C) Entrance to and Egress from Working Space.
(1) Minimum Required. At least one entrance of sufficient
area shall be provided to give access to and egress
from working space about electrical equipment.

If you bring you own ladder the space is accessible. Not easily or readily accessible, but that is not the requirement.

OK, but if I were the prospective homeowner, I'd be saying WTF, no thanks! Bad enough you stumble around in the dark if there is an issue, but now you have to go outside, dragging a step ladder, open an access way, set the ladder, and climb down with one hand while clutching a flashlight in the other?!?
 

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
OK, but if I were the prospective homeowner, I'd be saying WTF, no thanks! Bad enough you stumble around in the dark if there is an issue, but now you have to go outside, dragging a step ladder, open an access way, set the ladder, and climb down with one hand while clutching a flashlight in the other?!?

Is the GC paying the OP or the HO? If it's the GC, just do what he asks and let him take the flack. If it's the HO, consult with the HO and see what they want.

Oh, and code requires a light in the area.

110.26(D) Illumination. Illumination shall be provided for all
working spaces about service equipment, switchboards,
switchgear, panelboards, or motor control centers installed indoors
and shall not be controlled by automatic means only.
Additional lighting outlets shall not be required where the
work space is illuminated by an adjacent light source or as
permitted by 210.70(A)(1), Exception No. 1, for switched receptacles.
 

david

Senior Member
Location
Pennsylvania
Building contractor is asking me to install a residential service on a new construction project.

The panel will be located in the basement.

Conditions are;
- Pea gravel floor with pockets of standing water .
- No permanent or temporary stairs.
- Only access is through outdoor egress with about a 3' step down.

My thoughts are that the inspector will refuse entering because of accessibility.

Thoughts please.

most of the time the building contractor will have a ladder if the electrical inspector was made aware of the hours the building contractor would be on site

The Building contractor may be on a generator and might welcome an inspection on the
service

50 % of the homes built here are built without the site having a temp service
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
OK, but if I were the prospective homeowner, I'd be saying WTF, no thanks! Bad enough you stumble around in the dark if there is an issue, but now you have to go outside, dragging a step ladder, open an access way, set the ladder, and climb down with one hand while clutching a flashlight in the other?!?

I'm with you. Forget the code. This fails the good judgement and common sense test. I would never allow it in one of my properties.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Building contractor is asking me to install a residential service on a new construction project.

The panel will be located in the basement.

Conditions are;
- Pea gravel floor with pockets of standing water .
- No permanent or temporary stairs.
- Only access is through outdoor egress with about a 3' step down.

Wait.

Is this condition because the slab is not yet poured and no steps installed or is this how it's going to be?

-Hal
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Wait.

Is this condition because the slab is not yet poured and no steps installed or is this how it's going to be?

-Hal

OK, that is a fair question. I may have jumped the gun a bit. Let's see what the OP has to say.
 