Inspector correction: main dwelling feeder is passing in the footprint of the house

Alexis

Member
Location
Los Angeles
Hello,

Today I got a correction for something that I think is complete nonsense. I would appreciate your feedback:
1728578012958.png

My main conduit for the new 400A disconnect is passing throut the ceiling of the carport (he calles it "under the building") as it was requested by LADWP (Photos attached). He is trying to tell me to go around, on the side of the the building. Am I wrong here? The "code language" seems totally not applicable here?

The other violation he gave us is my 3in LB. I have 2 sets of 3/0 CU feeders coming down to the disconnect. In the LB it stated max 3x 250MCM. Does it then mean that we can't use any 3in LB for 400A services? As 1 set of 250MCM is too small and 2 sets of 3/0 too much.

Thank you so much for your feedback!
 

Attachments

  • Screenshot_20241010_092729_OneDrive.jpg
    Screenshot_20241010_092729_OneDrive.jpg
    176 KB · Views: 50
  • Screenshot_20241010_092648_Chrome.jpg
    Screenshot_20241010_092648_Chrome.jpg
    668.1 KB · Views: 50

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
I would have said 110.26(E)(2)(C) - The water pipe is in the dedicated space + spill protection from the water pipe. It could also be sewer. I can't tell.

If you need a ladder to get to the meter LADWP will prob fail you. I have never seen them okay with a meter that is above 6'3".

I don't see it as inside the building.

If you take the area of 3x250 and subtract it by the area of 6x3/0 then the inspector is right. 314.28(C)(3). Basically, the area that the conduit body is listed for can not be exceeded.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The other violation he gave us is my 3in LB. I have 2 sets of 3/0 CU feeders coming down to the disconnect. In the LB it stated max 3x 250MCM. Does it then mean that we can't use any 3in LB for 400A services? As 1 set of 250MCM is too small and 2 sets of 3/0 too much.
He's correct. Your conductor fill cannot exceed what's marked inside of the conduit body. You'll probably need some type of pull box if the POCO allows it ahead of the meters.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
The other violation he gave us is my 3in LB. I have 2 sets of 3/0 CU feeders coming down to the disconnect. In the LB it stated max 3x 250MCM.
The applicable code section is 314.28(A)(3), the last paragraph of which says:

"For other conductor sizes and combinations, the total cross-sectional area of the fill shall not exceed the cross-sectional area of the conductors specified in the marking, based on the type of conductor identified as part of the product listing."

The informational note after said the marking is based on XHHW insulation by default.

250 MCM XHHW conductors have a cross-sectional area including insulation of 251.9 mm2 per Chapter 9 Table 5. If you are using XHHW, then 3/0 Cu conductors have a cross-sectional area of 170.5 mm2. So if this is single phase and you have 4 of those for the ungrounded conductors, that leaves you with 3*251.9 - 4 *170.5 = 73.7 mm2. The largest grounded conductor that would fit is #2 Cu XHHW (ok, that cheats by 0.24 mm2).

But Table 250.102(C)(1) says the minimum size grounded conductor when the ungrounded conductors have a combined area of 500 MCM is 1/0 Cu. So there's not enough room for even the minimum size grounded conductor. And using THWN-2 instead of XHHW insulation doesn't help.

On this one the inspector is correct.

Cheers, Wayne
 

Alexis

Member
Location
Los Angeles
Thank you all so much for your responses, this helps a lot!

I'm very surprised that standard 3in LB can't support 400A when utility ESR directly calling for it.. I also just thought that we could use 2 pairs of 2/0, since we can use derating for the feeders in res building, but I think we are still slightly over.

Maybe in this case I may try to go 4in LB and use reducing bushings.. and will try to argue my way of moving the conduit and loosing day of work and more money in materials (current wires will be too short) for a made up correction
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Thank you all so much for your responses, this helps a lot!

I'm very surprised that standard 3in LB can't support 400A when utility ESR directly calling for it.. I also just thought that we could use 2 pairs of 2/0, since we can use derating for the feeders in res building, but I think we are still slightly over.

Maybe in this case I may try to go 4in LB and use reducing bushings.. and will try to argue my way of moving the conduit and loosing day of work and more money in materials (current wires will be too short) for a made up correction
If the conductors are 4 AWG and larger and the conduit is anywhere near a 40% fill, a standard conduit body will almost never be suitable.
You can use a larger conduit body with reducers as you suggested or a mogul conduit body designed for the purpose.
I like the Reddot MALB series but they are pricey. MALB-8
1728659997998.jpeg
 

Alexis

Member
Location
Los Angeles
If the conductors are 4 AWG and larger and the conduit is anywhere near a 40% fill, a standard conduit body will almost never be suitable.
You can use a larger conduit body with reducers as you suggested or a mogul conduit body designed for the purpose.
I like the Reddot MALB series but they are pricey. MALB-8
View attachment 2573822
Thank you for the advice. My 3in conduit fill is only 17.19% (6x3/0) so far from getting close, so that is one of the things that surpriced me. I usually used my conduit fill calculator with thinking that LBs will be matching it..
 
Last edited:

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Thank you for the advice. My 3in conduit fill is only 17.19% (6x3/0) so far from getting close, so that is one of the things that surpriced me. I usually used my conduit fill calculator with thinking that LBs will be matching it..
I really should not have mentioned fill as the issue is based on the required 6x of the conduit size between the openings for a 90° pull.

The volume only comes in when converting from the conductors shown on the LB and the ones that you are installing. See post #11.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Thank you for the advice. My 3in conduit fill is only 17.19% (6x3/0) so far from getting close, so that is one of the things that surpriced me. I usually used my conduit fill calculator with thinking that LBs will be matching it..
It's not just the volume fill but bend radius for the conductors.
 

kwired

Electron manager
Location
NE Nebraska
Thank you all so much for your responses, this helps a lot!

I'm very surprised that standard 3in LB can't support 400A when utility ESR directly calling for it.. I also just thought that we could use 2 pairs of 2/0, since we can use derating for the feeders in res building, but I think we are still slightly over.

Maybe in this case I may try to go 4in LB and use reducing bushings.. and will try to argue my way of moving the conduit and loosing day of work and more money in materials (current wires will be too short) for a made up correction
I see no reason you can't use 2 sets of 2/0 copper in parallel with the 83% rule but they would need to be in separate raceways. The table(depending on which NEC applies) simply says 400 copper for 400 amps.

If all in one raceway the required ampacity adjustment won't let it work, you end up with adjusted ampacity of 156 per conductor times 2 gives you net of 312. The 83 percent allowed for 400 amps is 332.
 
Top