Inspector is asking for a 3 pole gfi breaker on a plug in mixer for a pizza parlor. He won’t give the contractor the code he calling him out on.

Location
Orangevale
Occupation
Contractor semi retired
A inspector is wanting my contractor to put in a 3 pole 20 amp gfci breaker on a pizza dough mixer that has a cord that plugs into the wall. He won’t give the code he is calling out. Has anyone else ever heard of this before.
 

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
Understand that it's the receptacle, not the load that requires the GFCI protection.

Good catch. I didn't add that part. ** All the appliances that are cord and plug to a receptacle **


The only ones that might have to be at the breaker, even without cord and plug are from 422.5. Or if you are in the NEC 2023 they are in a separate part of 210.8.
 