Inspector is asking for a 3 pole gfi breaker on a plug in mixer for a pizza parlor. He won’t give the contractor the code he calling him out on.

Merry Christmas
Location
Orangevale
Occupation
Contractor semi retired
A inspector is wanting my contractor to put in a 3 pole 20 amp gfci breaker on a pizza dough mixer that has a cord that plugs into the wall. He won’t give the code he is calling out. Has anyone else ever heard of this before.
 

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
Understand that it's the receptacle, not the load that requires the GFCI protection.

Good catch. I didn't add that part. ** All the appliances that are cord and plug to a receptacle **


The only ones that might have to be at the breaker, even without cord and plug are from 422.5. Or if you are in the NEC 2023 they are in a separate part of 210.8.
 
Location
Colorado
Occupation
Electrical Design
Dealing with this very problem today. We added a receptacle with a three phase GFCI module for a third pizza oven in a stack configuration and now we are having nuisance tripping issues due to what I suppose is the electronics current leakage on the ground from one of the other existing ovens in the stack.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Dealing with this very problem today. We added a receptacle with a three phase GFCI module for a third pizza oven in a stack configuration and now we are having nuisance tripping issues due to what I suppose is the electronics current leakage on the ground from one of the other existing ovens in the stack.
Yep, anything with an inverter inside is going to be a headache for GFCIs.
 