Hey Guys,
I've got an inspector insisting that the two small appliance circuits in a residential kitchen can't serve any other receptacles other than the counter-top receptacles.
This is the first I've heard of this in over 20yrs in the trade. When I showed him the code sections below, he told be that the City goes by the 2019 CEC
(California Electrical Code) not the NEC. Well I just reviewed the CEC and of course its word for word the same.
Is this inspector an idiot, or I am missing something?
210.52(B)(1)
(B) Small Appliances
(1) Receptacle Outlets Served
In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
210.52(B)(3)
(3) Kitchen Receptacle Requirements
Receptacles installed in a kitchen to serve countertop surfaces shall be supplied by not fewer than two small-appliance branch circuits, either or both of which shall also be permitted to supply receptacle outlets in the same kitchen and in other rooms specified in 210.52(B)(1). Additional small-appliance branch circuits shall be permitted to supply receptacle outlets in the kitchen and other rooms specified in 210.52(B)(1). No small-appliance branch circuit shall serve more than one kitchen.
Thanks
I've got an inspector insisting that the two small appliance circuits in a residential kitchen can't serve any other receptacles other than the counter-top receptacles.
This is the first I've heard of this in over 20yrs in the trade. When I showed him the code sections below, he told be that the City goes by the 2019 CEC
(California Electrical Code) not the NEC. Well I just reviewed the CEC and of course its word for word the same.
Is this inspector an idiot, or I am missing something?
210.52(B)(1)
(B) Small Appliances
(1) Receptacle Outlets Served
In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
210.52(B)(3)
(3) Kitchen Receptacle Requirements
Receptacles installed in a kitchen to serve countertop surfaces shall be supplied by not fewer than two small-appliance branch circuits, either or both of which shall also be permitted to supply receptacle outlets in the same kitchen and in other rooms specified in 210.52(B)(1). Additional small-appliance branch circuits shall be permitted to supply receptacle outlets in the kitchen and other rooms specified in 210.52(B)(1). No small-appliance branch circuit shall serve more than one kitchen.
Thanks