Inspector requirement

Status
Not open for further replies.

friday

Member
I,m burying 2-2" pvc pipes for a doctors office. Service is 120/240 single phase and conduit is under a driveway. According to the code 24" cover is needed. My problem is this, the inspector neither passed nor failed me but insisted right before I reached the power pole , for utility hook up, that I buried these conduits with minimum 36" cover. Should I grab my shovel or argue the point of 24" cover. Does he have the right to make up his own rules beyond the NEC??
 
Re: Inspector requirement

Well does the area that you're working in have any local requirements that exceed or modify the NEC? If not than I say dig your heels in. Not into the ground but into arguing that he can only enforce what's in the book not what's in his head.
 
Re: Inspector requirement

If it is for our service cables, we require a 36" deep trench. The rules from the NESC match the NEC so it is just our rules. I suspect that Bob is correct in his assessment. :D
 
Re: Inspector requirement

I think the 36" depth also comes into play if you aren't bonding metal elbows. Could this be the problem?

STeve
 