I thought we were past the issue of whether or not a grid tie transformerless inverter is a separately derived system.
An inspector is asking us to install a separate SPD per NEC 285.24 (C) for separately derived systems on a residential gird tied solaredge inverter.
Is it still up for debate that grid tie inverters are not separately derived? Any helpful resource to help convince the inspector other than the obvious NEC definition of a separately derived system?
An inspector is asking us to install a separate SPD per NEC 285.24 (C) for separately derived systems on a residential gird tied solaredge inverter.
Is it still up for debate that grid tie inverters are not separately derived? Any helpful resource to help convince the inspector other than the obvious NEC definition of a separately derived system?