howdy folks , I have a job where we are going to turn the meter main panel into a sub panel , it's 100 A & feed it from a new 200 A service , we installed a ground rod because the HO didn't want us to disturb her pavers where the existing ground rod is . we will be feeding the soon to be 100 sub with 3 # 4 & i # 8 copper thhn , & installing a separate ground bar in the panel . the inspector showed up today & said we need 2 ground rods 6' apart due to the fact that there is no ufer ground for the new 200 service . what am I missing ? Im in northern Calif
tks
animal
tks
animal