brian john
Senior Member
- Location
- Leesburg, VA
Went to a job site to test a newly installed service (480/277 1200 amp), GFP test, Megger and micro-ohm the Main CB. The neutral ground bond was in the wrong location, I explained to the contractor they needed to relocate the connection. The contractor installed the neutral ground bond to the load side of the neutral CT. They told me they have done numerous 480/277 over 1000 amp services and the local inspector requires them to bond the service in this way.
They wanted me to write a letter as part of my test report stating why I requested they relocate the bond connection. If indeed the inspector has been telling contractors to install the bond connection in this manner does he have any liability?
It is one thing for an inspector to wrongly require you to install anti-shorts in MC cable, then for him to require you to improperly install a bond connection that could possibility result in "nuisance" tripping or additional damage from a desensitized GFP operation.
EDITED FOR INCORRECT WORDING.....
They wanted me to write a letter as part of my test report stating why I requested they relocate the bond connection. If indeed the inspector has been telling contractors to install the bond connection in this manner does he have any liability?
It is one thing for an inspector to wrongly require you to install anti-shorts in MC cable, then for him to require you to improperly install a bond connection that could possibility result in "nuisance" tripping or additional damage from a desensitized GFP operation.
EDITED FOR INCORRECT WORDING.....