eric9822
Senior Member
- Location
- Camarillo, CA
- Occupation
- Electrical and Instrumentation Tech
We are in the process of installing an eyewash station in a Class 1 Div 2 natural gas compressor yard, I rarely do any work in classified environments so I would like some input. The eyewash station has an integral flow switch with dry contacts that activates a local horn/strobe and also feeds back into the plant control system. The control system I/O and the power source are located outside of the classified area. From what I see in articles 500 and 501 it looks like the switch and local horn/strobe need to be listed for hazardous locations. Rigid threaded conduit and flexible liquidtite conduit are acceptable raceways. Seals and explosion proof conduit bodies are not required. Is this correct? Thanks.