Installation of low voltage (i.e.24vdc) conductors with

Status
Not open for further replies.

johnlangdon

New member
Q1-Existing control systems I have seen have the control air (80 psi) ran with control wiring (limit switches) through conduits to valves. Is this an approved installation? The only article I found was 300.8. Is there an exception somewhere?.
Q2-Can control air 80 psi or lower be ran with control wiring without barriers in control panels?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Installation of low voltage (i.e.24vdc) conductors with

John,
If the control circuits are Article 725 circuts, then 300.8 does not apply. See 725.3.
Don
 
Status
Not open for further replies.