BillK-AZ
Senior Member
- Location
- Mesa Arizona
Equipment: Solectria PVI 13kW inverter with front facing disconnects and internal DC Combiner
These inverters use external safety switches for the AC and DC disconnects. One option is to specify that the disconnects face forward, rather than to the sides. If the disconnects were facing the sides, clearance would be needed on the sides.
When the internal DC Combiner option is specified, the fuseholders and terminal block are crammed into the bottom area of the DC disconnect and almost cover the only rear concentric knockout that has a matching access hole in the bracket that mounts the disconnect to the inverter.
Since this is a concentric knockout and the voltage is over 250 volts, the conduit must be bonded with a ground bushing. But, the access to the concentric knockout is such that it is not possible to tighten the lock screw on the ground bushing. The installer has to carefully remove the factory installed fuseholders in order gain access to the screw. They should make the designers actually install these inverters.
In hindsight, it would have been better to have designed the system with a separate DC Combiner.
These inverters use external safety switches for the AC and DC disconnects. One option is to specify that the disconnects face forward, rather than to the sides. If the disconnects were facing the sides, clearance would be needed on the sides.
When the internal DC Combiner option is specified, the fuseholders and terminal block are crammed into the bottom area of the DC disconnect and almost cover the only rear concentric knockout that has a matching access hole in the bracket that mounts the disconnect to the inverter.
Since this is a concentric knockout and the voltage is over 250 volts, the conduit must be bonded with a ground bushing. But, the access to the concentric knockout is such that it is not possible to tighten the lock screw on the ground bushing. The installer has to carefully remove the factory installed fuseholders in order gain access to the screw. They should make the designers actually install these inverters.
In hindsight, it would have been better to have designed the system with a separate DC Combiner.