We have a customer that wants us to use a 3 phase transformer on a single phase system. It is a single phase 480/277 with a 120/208 output. Will this work properly? My concern is the derived neutral.
Both 480/277 and 120/208 are three phase voltages.We have a customer that wants us to use a 3 phase transformer on a single phase system. It is a single phase 480/277 with a 120/208 output. Will this work properly? My concern is the derived neutral.
It not necessarily totally useless, but definitely will not have full rated kVA ability. What can or can not work will depend on design of the transformer - Delta -wye, wye-wye, delta-delta, single core, multiple cores...No, it will not provide 120/240v. Nor will it provide 120/208v.
We have a customer that wants us to use a 3 phase transformer on a single phase system. It is a single phase 480/277 with a 120/208 output. Will this work properly? My concern is the derived neutral.
We only need single phase output. The contractor has a 3 phase temporary power sled and he was wanting to tie into an existing single phase 480V circuit for a temporary job shack using the transformer on the sled. this circuit is 1300' from the main project.
Me thinks he has power at the site but only has a 480 volt single phase circuit that he is interested in connecting to, and wants to tie into the transformer on the sled (and not use the generator, presuming there is also one on the sled).So you are asking whether you can use a 480-208Y120V 3 phase transformer, fed with 3 phase 480Y277V input from a generator, to feed a single phase panel with 120/208V using 2 hots and a neutral? If that's the case then yes, but the balance on the 3 phase side will be bad. Does that matter on a generated system? Probably not.
480V single phase without coming from a 3 phase transformer somewhere?Me thinks he has power at the site but only has a 480 volt single phase circuit that he is interested in connecting to, and wants to tie into the transformer on the sled (and not use the generator, presuming there is also one on the sled).
If so I think he can get 120 volts off one secondary phase, will only be 1/3 total kVA rating of the unit available for the most part.
480V single phase without coming from a 3 phase transformer somewhere?
OK, probably another of those things that you experience in your area that I never see in here, especially when it comes to farm services. I spent a lot of time working in farm country in the pacific Northwest though and I never came across 480V single phase services. But you've taught me that there are things out there that I never experience. Such is the value of a forum like this; lots of different perspectives.
You will only get 10 kVA @120 volts out of it. You will only energize one primary coil, it will only magnetically couple to one secondary coil.We have 2 legs of the 480v system. It feeds through a ground vault further on to a future gate transformer and 240v panel. He wants to set the job trailer next to the vault and use the temp service sled to feed his 240v trailer. The transformer is a 30KVA transformer with 3 coils with taps.
OK, one main issue and two other possible problematic scenarios then, depending on the EXACT nature of your transformer. Your initial information is not really clear. So first please clarify:We have 2 legs of the 480v system. It feeds through a ground vault further on to a future gate transformer and 240v panel. He wants to set the job trailer next to the vault and use the temp service sled to feed his 240v trailer. The transformer is a 30KVA transformer with 3 coils with taps.
It is a single phase 480/277 with a 120/208 output
What kVA capacity does the shack require?We only need single phase output. The contractor has a 3 phase temporary power sled and he was wanting to tie into an existing single phase 480V circuit for a temporary job shack using the transformer on the sled. this circuit is 1300' from the main project.