I am seeking input from you all........I need some guidance on
a proposed installation of a 300kw generator.
THE EXISTING CONDITIONS:
We currently have a building with an 800 amp service in it.
The MDP does not have a main disconnect in it.
THE PROPOSAL:
We have received a quote from an EC to:
(1) Provide & install 1 - 800 amp rated fused service rated
disconnect,
(2) Re-work the existing secondary service entrance conductors
& terminate to the line side of new main disconnect,
(3) Provide & install 3 - 3" emt raceways & 800 amp rated wire
from the load side of new main disconnect to a new Manual
Transfer Switch, located near the Generator..............We
specified the MTS vs. an ATS for our needs.
(4) Provide & install 1 - 800 amp rated Manual Transfer
Switch,
(5) Provide & install 3 - 3" emt raceways and 800 amp wire
from load side of new MTS to the existing MDP and connect,
(6) Provide & install 3 - 3" pvc raceways and 800 amp wire
underground from the Generator to the MTS. ( NOTE: All
raceways exposed to physical damage shall be RMC ),
(7) Provide & install required controls from the MTS to the
Generator,
(8) Provide & install required battery and block heater
circuit from existing electrical panel to Generator,
(9) Grounding & bonding as required,
(10) Testing
In the Quote, the EC states that all work shall be in
compliance with the NEC, but did not reference which
edition.
No information on the length of the raceways, ...type
of conductors, ...exactly how the Grounding & Bonding
would be accomplished, etc.
I do not know for sure, but the length of the raceways
from the Generator to the MDP could be approx. 200 ft.
This is all of the information that I currently have
available, but I will try to answer any questions that
you have.
If possible, ...please cite any discrepancies \ suggestions
\ other from the `05 NEC, as that will be the code of
reference for this project, although it has not been
[ officially ] stated by the EC.
Any input is welcomed, ...and "Much Thanks ! " :thumbsup:
FWIW, ...price is not necessarily the issue, however,
we DO want to ensure that we are getting a code compliant
install [ i.e. - use of Al conductors vs. Cu conductors ].
~ + ~ + ~
I am seeking input from you all........I need some guidance on
a proposed installation of a 300kw generator.
THE EXISTING CONDITIONS:
We currently have a building with an 800 amp service in it.
The MDP does not have a main disconnect in it.
THE PROPOSAL:
We have received a quote from an EC to:
(1) Provide & install 1 - 800 amp rated fused service rated
disconnect,
(2) Re-work the existing secondary service entrance conductors
& terminate to the line side of new main disconnect,
(3) Provide & install 3 - 3" emt raceways & 800 amp rated wire
from the load side of new main disconnect to a new Manual
Transfer Switch, located near the Generator..............We
specified the MTS vs. an ATS for our needs.
(4) Provide & install 1 - 800 amp rated Manual Transfer
Switch,
(5) Provide & install 3 - 3" emt raceways and 800 amp wire
from load side of new MTS to the existing MDP and connect,
(6) Provide & install 3 - 3" pvc raceways and 800 amp wire
underground from the Generator to the MTS. ( NOTE: All
raceways exposed to physical damage shall be RMC ),
(7) Provide & install required controls from the MTS to the
Generator,
(8) Provide & install required battery and block heater
circuit from existing electrical panel to Generator,
(9) Grounding & bonding as required,
(10) Testing
In the Quote, the EC states that all work shall be in
compliance with the NEC, but did not reference which
edition.
No information on the length of the raceways, ...type
of conductors, ...exactly how the Grounding & Bonding
would be accomplished, etc.
I do not know for sure, but the length of the raceways
from the Generator to the MDP could be approx. 200 ft.
This is all of the information that I currently have
available, but I will try to answer any questions that
you have.
If possible, ...please cite any discrepancies \ suggestions
\ other from the `05 NEC, as that will be the code of
reference for this project, although it has not been
[ officially ] stated by the EC.
Any input is welcomed, ...and "Much Thanks ! " :thumbsup:
FWIW, ...price is not necessarily the issue, however,
we DO want to ensure that we are getting a code compliant
install [ i.e. - use of Al conductors vs. Cu conductors ].
~ + ~ + ~