I am installing a 180KW industrial water heater at my facility.
This is a 480V device and the vendor claims that the FLA is 216.51 amps. I am wondering if I can feed it from an existing 480V, 250A panel that's completely unloaded right now. The feed coming in to this panel is protected by a 250A breaker. The feed out to the water heater will also be protected by a 250A breaker.
I am pretty sure that this complies with code requirements, but do I run the risks of nuisance trips?
The load is non-continuous and I will almost never run this heater at full load. However, it is possible that we may have to run it at or near full load for an 8-minute cycle. Can a regular 250A breaker carry 216.51 amps for more than just a few seconds?
This is a 480V device and the vendor claims that the FLA is 216.51 amps. I am wondering if I can feed it from an existing 480V, 250A panel that's completely unloaded right now. The feed coming in to this panel is protected by a 250A breaker. The feed out to the water heater will also be protected by a 250A breaker.