We have a fleet gasoline dispenser at our facility. There is a containment sump below the dispenser. I need to add a liquid sensor in this sump. The sensor, in conjunction with the alarm system it connects to, is listed as intrinsically safe (UL Class I, Div 1, Group D). The sensor and alarm are made by Morrison Brothers:
Sensor: Model 924LS
Alarm: Model 918Q
My understanding is that this sensor does not require explosion-proof conduit & fittings. I intend to use RMC conduit to bring the alarm wires into the sump, then install a standard (non-hazardous location) threaded aluminum LB condulet. The sensor will thread into, and be suspended in the sump by, the LB. The splices between the sensor wiring and the wires running to the alarm will be made up inside the condulet. Duct seal will be packed around the alarm wires where they enter the condulet from the RMC in order to prevent the passage of vapors.
Does this sound correct?
I don't believe it's required, but I think it would be prudent add a seal-off on the alarm wire RMC where it exits the ground (outside the Class 1, Div 2 zone) and transitions to EMC to the alarm box.
Does this sound reasonable?
Additional questions:
Are there minimum spacing requirements in the ground between this alarm RMC conduit and the RMC conduit that supplies power to the dispenser?
Are there minimum spacing requirements between the alarm EMC conduit and any power EMC conduit that is above-ground (on the outside of a building, beyond the Class 1, Div 2 zone)?
Does there need to be any bonding of the metallic conduit containing the alarm wiring?
Sensor: Model 924LS
Alarm: Model 918Q
My understanding is that this sensor does not require explosion-proof conduit & fittings. I intend to use RMC conduit to bring the alarm wires into the sump, then install a standard (non-hazardous location) threaded aluminum LB condulet. The sensor will thread into, and be suspended in the sump by, the LB. The splices between the sensor wiring and the wires running to the alarm will be made up inside the condulet. Duct seal will be packed around the alarm wires where they enter the condulet from the RMC in order to prevent the passage of vapors.
Does this sound correct?
I don't believe it's required, but I think it would be prudent add a seal-off on the alarm wire RMC where it exits the ground (outside the Class 1, Div 2 zone) and transitions to EMC to the alarm box.
Does this sound reasonable?
Additional questions:
Are there minimum spacing requirements in the ground between this alarm RMC conduit and the RMC conduit that supplies power to the dispenser?
Are there minimum spacing requirements between the alarm EMC conduit and any power EMC conduit that is above-ground (on the outside of a building, beyond the Class 1, Div 2 zone)?
Does there need to be any bonding of the metallic conduit containing the alarm wiring?