300.4(E) Cables and Raceways Installed Under Roof Decking. A cable- or raceway-type wiring method, installed in exposed or concealed locations under metal-corrugated sheet roof decking, shall be installed and supported so the nearest outside surface of the cable or raceway is not less than 38 mm (1? in.) from the nearest surface of the roof decking.
FPN: Roof decking material is often repaired or replaced after the initial raceway or cabling and roofing installation and may be penetrated by the screws or other mechanical devices designed to provide ?hold down? strength of the waterproof membrane or roof insulating material.
Exception:  Rigid metal conduit and intermediate metal conduit shall not be required to comply with 300.4(E).