Hi Guys
This question pertains to an indoor residential application (garage). Washington state, USA.
I would like to install a surface mount, 240v fused disconnect adjacent to (within 10ft) a flush mounted 200A panelboard. The panelboard bus is full, so I will be feeding the disconnect from the feed-through lugs. Tap rules require that conductors be enclosed in a raceway (240.21). A 240v surface mounted receptacle will be wired in EMT to the disconnect.
I'm looking for some advice. Can I run the feeders to the disconnect in steel flex from the side of the panel to the back of the disconnect, all behind drywall? Does the sheath on SER cable count as a raceway? Maybe there is a cleaner way to do this that I'm not thinking of.
Thank You!
This question pertains to an indoor residential application (garage). Washington state, USA.
I would like to install a surface mount, 240v fused disconnect adjacent to (within 10ft) a flush mounted 200A panelboard. The panelboard bus is full, so I will be feeding the disconnect from the feed-through lugs. Tap rules require that conductors be enclosed in a raceway (240.21). A 240v surface mounted receptacle will be wired in EMT to the disconnect.