iwire2
Member
- Location
- Houston, Texas
I have two panelboards on the secondary of a 480-120/208V Wye 75kVA transformer. From the secondary of the transformer, each panelboard is fed with its own set of conductors (250 MCM THHN Copper, phase and neutral) in separate conduits. The transformer has one primary feed which is protected at not more than 125% of rated primary current (Primary is 125 amp breaker with #1 THHN Copper conductors). Each 3 phase 120/208 volt panelboard has a 250 amp MCB.
Is this code compliant, as you can have multiple (up to six sets of secondary breakers) on secondary of the transformer, but it states where secondary protection is required (not sure that it is, as it has primary protection) they must be grouped, (which they are), and the total of all the device ratings shall not exceed the the allowable value of a single overcurrent device (which they do not, as 250 amp x 2 panels exceeds the 250 amp total allowed).
Basically, I am thinking that if secondary protection is not required then 450.3 (A) or (B), Note 2 would not apply, and this installation is code compliant?:?
Is this code compliant, as you can have multiple (up to six sets of secondary breakers) on secondary of the transformer, but it states where secondary protection is required (not sure that it is, as it has primary protection) they must be grouped, (which they are), and the total of all the device ratings shall not exceed the the allowable value of a single overcurrent device (which they do not, as 250 amp x 2 panels exceeds the 250 amp total allowed).
Basically, I am thinking that if secondary protection is not required then 450.3 (A) or (B), Note 2 would not apply, and this installation is code compliant?:?