What is the rule of thumb when sizing motor circuit breakers uses in a breaker/starter/overload arrangement for a motor. I am aware that the instantaneous breakers in this case are only for short circuit protection and that the NEC allows the max short circuit setting to be 8X FLA. I also understand that with adjustable trip instantaneous breakers, the trip rating is not necessarily the rating of the breaker but is a range from 3X to 10X the rating of the breaker. In other words an adjustable 100A instant breaker has a trip setting range of 300 to 1000A.
So with that said, is there a rule of thumb or a general range for using these breakers with certain motors. As an example, if i have a 40hp motor @480V with a FLA of 47A what size breaker can I use. Can I theoretically use any size that will let me go up to 8X the FLA rating or in this case 376A. I know the code has an exception to allow the breaker setting to be up to 17X FLA for hard to start motors, should this number be taken into consideration.
Back to the 40hp, 47A example, if all I have avaliable is a 100A breaker I feel comfortable using it b/c 8X 47A is 376A which is well within the span of this breaker setting. Is this correct?
So with that said, is there a rule of thumb or a general range for using these breakers with certain motors. As an example, if i have a 40hp motor @480V with a FLA of 47A what size breaker can I use. Can I theoretically use any size that will let me go up to 8X the FLA rating or in this case 376A. I know the code has an exception to allow the breaker setting to be up to 17X FLA for hard to start motors, should this number be taken into consideration.
Back to the 40hp, 47A example, if all I have avaliable is a 100A breaker I feel comfortable using it b/c 8X 47A is 376A which is well within the span of this breaker setting. Is this correct?