instantaneous brkr

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
Hi
I used an 175A instantaneous brkr (upto 800% of load) equipped with shunt-trip
right after existing main breaker that 28 KVA elevator via existing 100A feeder
Right???

elevator company want 175A brkr with shunt-trip
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Assuming you mean instantaneous trip ONLY circuit breaker, outside of a factory built combination motor starter, there is no valid/legal use for it. The only reason you can buy them is to use for exact replacement in a motor starter.
 

Ingenieur

Senior Member
Location
Earth
I don't think he using this for nec required electrical protection
but as an A17 and NFPA code required auto disconnect
the shaft is sprinklered
heat detectors are located in close proximity with a slightler lower rating than the sprinkler heads
the detectors trip the shunt, a td is often allowed to park the car at a landing
local manual reset is required

imo, not an issue
 

topgone

Senior Member
Hi
I used an 175A instantaneous brkr (upto 800% of load) equipped with shunt-trip
right after existing main breaker that 28 KVA elevator via existing 100A feeder
Right???

elevator company want 175A brkr with shunt-trip

All elevator controls are required to have the normal starter protections (overload, stall protection and instantaneous trip protection during faults). When the elevator shaft is is sprinklered, an additional shunt trip is required to disconnect power to the elevator, the tripping signal taken from the fire protection controller.
 

Codegui2

Member
Location
Lodi Ca USA
Is it a fire alarm breaker now?

Is it a fire alarm breaker now?

Would you expect this breaker to now require a lock-on device at the breaker handle similar to a fire alarm power breaker?
 