What is the minimum instantaneous breaker settings in amps needed for a three-phase, 200Hp, 575 volt rated code B motor?
Per Table 430.250 FLC = 192 A.
Per Table 430.52 for AC polyphase motors other than wound rotor:
800% of FLC = 1536 A.
Per Table 240.6(A) CB should be 1200 A.
However, per Table 430.7(B) LR is 3.54,
So, 200 hp * 3.54 = 708 kVA
So I = 711 A
Per Table 240.6(A) CB should be 800 A.
Which one is accurate?
Per Table 430.250 FLC = 192 A.
Per Table 430.52 for AC polyphase motors other than wound rotor:
800% of FLC = 1536 A.
Per Table 240.6(A) CB should be 1200 A.
However, per Table 430.7(B) LR is 3.54,
So, 200 hp * 3.54 = 708 kVA
So I = 711 A
Per Table 240.6(A) CB should be 800 A.
Which one is accurate?