I had a question regarding what is the best practice to set the Instantaneous setting on a relay which feeds a downstream MV switchgear lineup. For instance if I have a 4.16k Swichgear Bus A which has a feeder relay which feeds a downstream 4.16kV Switchgear Bus B containing a Main, Tie, and Feeder relays what should the feeder relay at Bus A have its Instantaneous setting set to?
I know that at the downstream Bus B the Main relay and Tie relay will have its Instantanous setting turned off so that it does not nusiance trip for Instantaneous faults downstream of the feeder relays on that bus, but what about the upstream feeder relay in Bus A? Should it also have its Inst setting turned off so not to nusiace trip for faults downstream of feeders in Bus B or should it be set so that it is above fault current at Bus B so that it does not pickup for faults at Bus B but still protects the feeder cable between Bus A and Bus B?
I'm looking for some setting guidelines for this type of scenario.
Thanks
I know that at the downstream Bus B the Main relay and Tie relay will have its Instantanous setting turned off so that it does not nusiance trip for Instantaneous faults downstream of the feeder relays on that bus, but what about the upstream feeder relay in Bus A? Should it also have its Inst setting turned off so not to nusiace trip for faults downstream of feeders in Bus B or should it be set so that it is above fault current at Bus B so that it does not pickup for faults at Bus B but still protects the feeder cable between Bus A and Bus B?
I'm looking for some setting guidelines for this type of scenario.
Thanks