- Junior plan reviewer
I have on plans instantaneous water heater 10kw at 277V single phase. The breaker size provided on plans is 50A. The full load amps of heater comes out to 36.10a.
The water heater manufacturer instruction recommends minimum branch circuit cable size of #8 awg at 75 deg C. The instruction says protected by the correctly rated circuit breaker but does not say the size nor if water heater is considered continuous or non continuous load.
The water heater is Eemax Spex100T. Below link is the water heater’s instruction manual:
Question:
1. Where does NEC 2017 section 422 talk about instantaneous water heater breaker sizing?
2. What size is the breaker should be based on instructions and NEC 2017? It gets confusing
The water heater manufacturer instruction recommends minimum branch circuit cable size of #8 awg at 75 deg C. The instruction says protected by the correctly rated circuit breaker but does not say the size nor if water heater is considered continuous or non continuous load.
The water heater is Eemax Spex100T. Below link is the water heater’s instruction manual:
Question:
1. Where does NEC 2017 section 422 talk about instantaneous water heater breaker sizing?
2. What size is the breaker should be based on instructions and NEC 2017? It gets confusing