hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have 4.1kw, 277V single phase instantaneous water heater full load amps of 14.8A. The breaker provided is 20A. Since instant water heater is non continuous load should not the breaker be sized 15A?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I have 4.1kw, 277V single phase instantaneous water heater full load amps of 14.8A. The breaker provided is 20A. Since instant water heater is non continuous load should not the breaker be sized 15A?
In my opinion that would be too little headroom for any type of load.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I have 4.1kw, 277V single phase instantaneous water heater full load amps of 14.8A. The breaker provided is 20A. Since instant water heater is non continuous load should not the breaker be sized 15A?
I tend to agree it is noncontinuous but I would be using a 20 A cb.
 