Instantenous water heater

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have 4.1kw, 277V single phase instantaneous water heater full load amps of 14.8A. The breaker provided is 20A. Since instant water heater is non continuous load should not the breaker be sized 15A?
 
I have 4.1kw, 277V single phase instantaneous water heater full load amps of 14.8A. The breaker provided is 20A. Since instant water heater is non continuous load should not the breaker be sized 15A?
In my opinion that would be too little headroom for any type of load.
 
I have 4.1kw, 277V single phase instantaneous water heater full load amps of 14.8A. The breaker provided is 20A. Since instant water heater is non continuous load should not the breaker be sized 15A?
I tend to agree it is noncontinuous but I would be using a 20 A cb.
 
Status
Not open for further replies.
Top