Do circuits for transformer instrumentation protective devices such as liquid level, sudden pressure and temperature require an EGC be run with the conductors ?


Sent from my iPhone using Tapatalk
 

Dale001289

Senior Member
Location
Georgia
I don’t think you’d need an EGC. What you described probably falls under 725, Class 2 inherently limited circuit.


Sent from my iPhone using Tapatalk
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
What voltage and they located in classified area?
For the Class 2 limited energy I ran in normal areas, an EGC was not required by the NEC, but often required by job specs
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
As with most Code, few rules are written in stone, but generally circuits less than 50 volts don't require grounding (see 250.20) but there are exceptions in Art 250 itself an for certain locations.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
What voltage and they located in classified area?
For the Class 2 limited energy I ran in normal areas, an EGC was not required by the NEC, but often required by job specs

Thanks Tom. This is an unclassified area.


Sent from my iPhone using Tapatalk
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
As with most Code, few rules are written in stone, but generally circuits less than 50 volts don't require grounding (see 250.20) but there are exceptions in Art 250 itself an for certain locations.
It does not exactly actually say that. In any case, I think the OP is asking about an EGC and not whether a grounded conductor is required.
 