Instr circuits for transformer protective devices
Isaiah
Baton Rouge
Electrical Inspector
Do circuits for transformer instrumentation protective devices such as liquid level, sudden pressure and temperature require an EGC be run with the conductors ?
I don’t think you’d need an EGC. What you described probably falls under 725, Class 2 inherently limited circuit.
What voltage and they located in classified area?
For the Class 2 limited energy I ran in normal areas, an EGC was not required by the NEC, but often required by job specs
As with most Code, few rules are written in stone, but generally circuits less than 50 volts don't require grounding (see 250.20) but there are exceptions in Art 250 itself an for certain locations.
Thanks Tom. This is an unclassified area.
It does not exactly actually say that. In any case, I think the OP is asking about an EGC and not whether a grounded conductor is required.