Is there a code or requirements of communication separation other than Article 300. I have and MCC with communication and power running in the same cable tray. I know the NEC doesn't care if the system fails, but is there a reference or guide line for communication and power cabling?


Sent from my iPhone using Tapatalk
 
Thank you, Yes 725.51 c show 725.121 Power Sources for Class 2 and Class 3 Circuits. (A) Power Source. The power source for a Class 2 or a Class 3 circuit shall be as specified in 725.121(A)(1), (A)(2), (A)(3), (A)(4), or (A)(5):

FPN No. 1: Figure 725.121 illustrates the relationships be- tween Class 2 or Class 3 power sources, their supply, and the Class 2 or Class 3 circuits.

FPN No. 2: Table 11(A) and Table 11(B) in Chapter 9 provide the requirements for listed Class 2 and Class 3 power sources.

(1) A listed Class 2 or Class 3 transformer (2) A listed Class 2 or Class 3 power supply (3) Other listed equipment marked to identify the Class 2 or Class 3 power source

Exception No. 1 to (3): Thermocouples shall not require listing as a Class 2 power source



Sent from my iPhone using Tapatalk
 
Am still confuse
It's not rocket science... it's actually worse. :lol:

Kidding aside, power to one side of tray, control to the other, physical barrier (divider) in between. If you also have communications cables, three sections, two dividers.
 
6779a0187c5ee6e2fd83adb12e3c5ebd.jpg
is this a violation for you.. it inside an mcc and there is 480 mix with controls wiring inside the panel if so can you tell me where i can find it


Sent from my iPhone using Tapatalk
 
... is this a violation for you.. it inside an mcc and there is 480 mix with controls wiring inside the panel if so can you tell me where i can find it
BTW that's not cable tray as defined by the NEC. That's wiring duct.
http://www.panduit.com/en/products-...routing-protection-and-insulation/wiring-duct

The NEC offers some restriction on separation inside enclosures, but it far from ideal. Perhaps take a look at NFPA 79 Electrical Standard for Industrial Machinery
http://www.nfpa.org/codes-and-stand...ds/list-of-codes-and-standards/detail?code=79
 
That application may fall under UL 508A, if its a control panel.
I run control and signaling in that type of duct together with power wiring, but only 120V. Never 480
 
That application may fall under UL 508A, if its a control panel.
I run control and signaling in that type of duct together with power wiring, but only 120V. Never 480
It is my understanding that UL508 does not apply to field wiring... unless that field wiring is between panels or equipment and furnished by the manufacturer as part of the listed product. I believe NFPA 79 says the same thing.
 