We have a project where the GC wants to spray fireproofing over our EMT conduits. Would this change our ambient temperature adjustment? If so, how would it be calculated?
I too have had similar questions related to NM and spray foam insulation, seems to me it would, but told not, no satisfactory answer has been given nor code/UL references either way. If someone with knowledge has definitive references that would be great.We have a project where the GC wants to spray fireproofing over our EMT conduits. Would this change our ambient temperature adjustment? If so, how would it be calculated?
There is no NEC requirement to even consider this, if there were then the NEC would provide a way to calculate it. Cables and conduits are run in insulation all of the time.
I don’t see a difference between a conduit buri in dirt and a conduit encased in insulation.
Same thermal affect.