I know a pool panel needs an insulated GND conductor, but is that in addition to the regular EGC?
D donw Senior Member Location Arizona Sep 23, 2010 #1 I know a pool panel needs an insulated GND conductor, but is that in addition to the regular EGC?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Sep 23, 2010 #2 No, the egc just needs to be insulated.
D donw Senior Member Location Arizona Sep 23, 2010 #3 Thanks, Dennis. Someone tried to tell me that it needed both.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Sep 23, 2010 #4 donw said: Thanks, Dennis. Someone tried to tell me that it needed both. Click to expand... Ask him how you would hook it up at the panel. 2 hots, one neutral and 2 grounds--- doesn't make sense does it.
donw said: Thanks, Dennis. Someone tried to tell me that it needed both. Click to expand... Ask him how you would hook it up at the panel. 2 hots, one neutral and 2 grounds--- doesn't make sense does it.
electricmanscott Senior Member Location Boston, MA Sep 23, 2010 #5 donw said: Thanks, Dennis. Someone tried to tell me that it needed both. Click to expand... Punch him in the throat.
donw said: Thanks, Dennis. Someone tried to tell me that it needed both. Click to expand... Punch him in the throat.