kenaslan
Senior Member
- Location
- Billings MT
Does anyone know of any reason that an underground ground ring would be insulated? It seems to me that an insulated ground wire defeats the purpose.
Ken
Ken
Given that "contact with planet Earth" is the purpose of a grounding electrode system, I would have to agree with you. Did you really encounter this, either as in design document (plans or specs) or in the field? That would be extraordinary.kenaslan said:It seems to me that an insulated ground wire defeats the purpose.
LarryFine said:They've never heard of zinc oxide?
Their concern is with corrosion of the pipe. In galvanic corrosion, steel will sacrifice itself to the copper in a grounding system. If the grounding system is galvanized steel, this is not a problem.kenaslan said:It is in a specification for the grounding system of a gas pipeline, I now have found out they want to use galv cable instead of copper. I was told that copper oxidizes. Hmm after 30+ years in the industry I must have been doing it wrong all this time, LOL