Would an equipment ground be required to be insulated if direct buried and part of a 4 wire single phase feeder?
Would an equipment ground be required to be insulated if direct buried and part of a 4 wire single phase feeder?
Vice Versa?
Vice Versa?
250.120(B) Aluminum and Copper-Clad Aluminum Conductors.
Equipment grounding conductors of bare or insulated aluminum
or copper-clad aluminum shall be permitted. Bare
conductors shall not come in direct contact with masonry or
the earth or where subject to corrosive conditions. Aluminum
or copper-clad aluminum conductors shall not be terminated
within 450 mm (18 in.) of the earth.
No, you cannot direct bury bare AL
Yes, but look at post 2, you said the opposite by mistake.