Insulated grounding conductor - 680

Status
Not open for further replies.

ArcLazerbeam

Member
Location
VT
Is there any particular reason the code requires the grounding conductor to be insulated once the wiring method is considered outside? It's not a requirement for other outdoor installations. Are they afraid of rusting EMT????
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Is there any particular reason the code requires the grounding conductor to be insulated once the wiring method is considered outside? It's not a requirement for other outdoor installations. Are they afraid of rusting EMT????

Maybe because in a pool environment potential differences on the order of a volt can cause shock? Making contact with a grounding conductor that is carrying either fault current or unexpected neutral current a hazard?
Or maybe it is just corrosion in a chlorine rich environment, even in open air?
 