Having difficulties interpreting the code for this application. Installed a 6-3 copper romex wire to a 50 amp dissconnect with a GFCI breaker 50 amp. On the load side of the dissconnect, I installed a 6-3 romex jacket still attached, inside of a 3/4 carflex to the control board the copper grounding conductor was uninsulated. The inspector said that the copper grounding wire had to be insulated starting from the inside of the dwelling to the dissconnect and then the load side of the dissconnect...He sited article 680.42 (C)
I corrected the problem as per 680.42 C and installed an insulated #12 grounding conductor .. The inspector said that I needed a #10 for a 6-3 conductor. I said that as per article 680.42 (C) The copper equipment grounding conductor THAT IS INSULATED OR ENCLOSED WITHIN THE OUTER SHEATH OF THE WIRING METHOD AND NOT SMALLER THAN #12 AWG SHALL BE PERMITTED TO BE USED FOR THE CONNECTON TO MOTOR,HEATING AND CONTROL LOADS THAT ARE PART OF A SELF CONTAINED SPA OR HOT TUB ASSEMBLY...
1. Why does the copper ground have to be insulated going from the dissconnect!?
2. I understand that a #10 wire is the copper ground for #6 copper but 680.42 (C) says not smaller than #12 why can't you use #12!? Like the code article states!?
Can anyone out there help me in interpreting this!?
Chris Michaels
Grandmastc@aol.com
Chris Michaels
Grandmastc@aol.com