I am on the road so do not have my code book readily available and looking for some assistance.
Context: Currently have a large project underway with several lighting control panels per floor across 5 different stories of the building.
Engineers have 8-10 switch legs on 1 branch circuit due to the intricacy of the spaces being lit.
All control panels have feed thru relays.
All rooms are laid out pretty typical with panelboard on left, relay panel on right, 2” gunners up to a trough/wireway with switch legs entering the top of the trough, and the branch circuit hot and neutral passing from the panel up to trough and back down into the relay panel.
Have had some back and forth on the legality of an insulated neutral bar in the wireway to connect all the grounded conductors of the switch legs to the grounded
Conductor from the panel, in order to avoid multiple neutral splices per circuit.
The question being: Is an insulated neutral bar installed “exposed” within a wireway a violation of the NEC? One of my journeymen is adamant that the neutral connections must be insulated to some degree (wirenut/wago/terminal blocks). I disagree, but would appreciate some input from folks with a code book at hand.
The neutral/grounded conductor of the circuit will still be contained within the same conduit as the ungrounded conductor from origin at panelboard to terminations at the relay panel.
Context: Currently have a large project underway with several lighting control panels per floor across 5 different stories of the building.
Engineers have 8-10 switch legs on 1 branch circuit due to the intricacy of the spaces being lit.
All control panels have feed thru relays.
All rooms are laid out pretty typical with panelboard on left, relay panel on right, 2” gunners up to a trough/wireway with switch legs entering the top of the trough, and the branch circuit hot and neutral passing from the panel up to trough and back down into the relay panel.
Have had some back and forth on the legality of an insulated neutral bar in the wireway to connect all the grounded conductors of the switch legs to the grounded
Conductor from the panel, in order to avoid multiple neutral splices per circuit.
The question being: Is an insulated neutral bar installed “exposed” within a wireway a violation of the NEC? One of my journeymen is adamant that the neutral connections must be insulated to some degree (wirenut/wago/terminal blocks). I disagree, but would appreciate some input from folks with a code book at hand.
The neutral/grounded conductor of the circuit will still be contained within the same conduit as the ungrounded conductor from origin at panelboard to terminations at the relay panel.