Having a discussion recently as to whether or not an EMT connector with an insulated throat meets the intent of 300.4(G) (when used with conductors #4 and larger) in lieu of a plastic bushing. My opinion is that they are complaint because they meet the requirement of the last sentence because they are fastened in place.
300.4(G) Insulated Fittings. Where raceways contain 4 AWG or larger insulated circuit conductors, and these conductors enter a cabinet, a box, an enclosure, or a raceway, the conductors shall be protected by an identified fitting providing a smoothly rounded insulating surface, unless the conductors are separated from the fitting or raceway by identified insulating material that is securely fastened in place.