Hi,
When I reviewed the NEC 392 (Cable tray), there is restriction of single conductor to 1/0 and larger.
Also, equipment grounding wire has to be bigger than 4AWG.
In table 392.10 (A) Wiring Methods, I can't find the insualted single wire like type THHN, THWN and XHHW.
My questions are
1. Do I have to understand that insulated single wire has to be bigger than 1/0?
2. Is there any way to use smaller size like 6AWG ground wire for circuit?
Thank you!