Insulated wire like THHN XHHW on cable tray

eunji

New User
Location
NC
Occupation
Engineer
Hi,

When I reviewed the NEC 392 (Cable tray), there is restriction of single conductor to 1/0 and larger.
Also, equipment grounding wire has to be bigger than 4AWG.
In table 392.10 (A) Wiring Methods, I can't find the insualted single wire like type THHN, THWN and XHHW.

My questions are
1. Do I have to understand that insulated single wire has to be bigger than 1/0?
2. Is there any way to use smaller size like 6AWG ground wire for circuit?

Thank you!
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Close....
Single conductors need to be 1/0 OR larger (not larger than 1/0)
EGC must be #4 or larger {see 392.10(B)(2)}
Conductors such as THWN-2 and XHHW can be obtained with CT rating.
 
Last edited:

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Close....
Single conductors need to be 1/0 OR larger (not larger than 1/0)
EGC must be #4 or larger {see 392.10(B)(2)}
Conductors such as THWN-2 and XHHW can be obtained with CT rating.
That's why you run it as a cable with a CT rating.
 